    2GIG Smoke Detector 5808W3/SMKT2/SMKT3 Programming/Installation

    How to: install smoke detectors. If you are not sure what type you have, unscrew detector from base, and check model number on bottom

    Download the cheat sheet for naming your sensors (descriptors)
    http://2gig.com/pdf/product-info/Che...et(Z-WAVE).pdf

    Do not install near vents, near bathrooms, or less than 4" from wall on ceiling. If installed on wall, top of detector no more than 12", no less than 4" from the ceiling.

    Ideal location/Code requirement is at staircases, outside and inside bedrooms.



    Programming
    Smoke Detector

    Access system configuration (logo>installer code> system configuration)
    Use right arrow to find an empty/unused zone
    Down arrow
    Change unused to (09) 24-hour fire
    Down arrow
    Enter (1058) for smkt3, or (0895) for smkt2, or for 5808w3 (0589)
    Down arrow
    Learn serial by shift then learn and tampering smoke det
    Down arrow
    Equip age (0) new
    Down arrow
    Loop 1(1)
    Down arrow
    Enter descriptor (insert, then code for each word as shown on cheat sheet)
    Down arrow
    Reports enabled (1)
    Down arrow
    Supervised enabled (1)
    Down arrow
    Chime disabled (00)
    Down arrow
    Summary screen (check it carefully, make sure programming is right)
    Then 'skip', 'end', 'exit'
    Panel reboots

    Smkt2 are heat and photo smokes on same zone, smkt3 on the other hand, have 3 separate zones to be programmed (smoke/heat/freeze)

    The above instructions are for both on smoke, but for a smkt3, you now have to program the heat zone...

    In system config use right arrow to find next empty zone
    Only three things will be different...equipment age becomes (2) 'Existing', loop is loop2 (2), and descriptor will be for heat (example, 'third floor smoke detector' on the loop1 zone becomes 'third floor heat detector' on loop2 zone)

    Heat Detector

    Change unused to (09) 24-hour fire
    Down arrow
    Enter (1058) for smkt3
    Down arrow
    Learn serial by shift then learn and tampering smoke det
    Down arrow
    Equip age (1) existing
    Down arrow
    Loop 2 (2)
    Down arrow
    Enter descriptor (I.e., "third floor heat detector")
    Down arrow
    Reports enabled (1)
    Down arrow
    Supervised enabled (1)
    Down arrow
    Chime disabled (00)
    If you decide to do freeze, process is same, for setting up heat zone, but instead of 24 hour fire, its 24 hour auxiliary, instead of loop2, it is loop3 (3) zone, and descriptor is for example 'third floor freeze detector'

    Freeze Alert

    Change unused to (08) 24-hour auxiliary
    Down arrow
    Enter (1058) for smkt3
    Down arrow
    Learn serial by shift then learn and tampering smoke det
    Down arrow
    Equip age (1) existing
    Down arrow
    Loop 3 (3)
    Down arrow
    Enter descriptor (I.e., "third floor freeze detector")
    Down arrow
    Reports enabled (1)
    Down arrow
    Supervised enabled (1)
    Down arrow
    Chime disabled (00)

  2. #2
    Junior Member
    Join Date
    Dec 2014
    Location
    Milwaukee, WI
    Posts
    15

    Boy, you're just a wealth of information! I programmed my smkt3 for heat & freeze per your instructions. Do you happen to to have a sheet with new descriptors? The older ones prior to firmware 1.13 are off a bit since they added more descriptors.

    Also, I know this post is old but the only thing that changed is for freeze alert. When you enter '(08) 24-hour auxiliary' there is no option for smkt3. Now it says 'freeze'.

  3. #3
    Quote Originally Posted by tattoohead View Post
    Boy, you're just a wealth of information! I programmed my smkt3 for heat & freeze per your instructions. Do you happen to to have a sheet with new descriptors? The older ones prior to firmware 1.13 are off a bit since they added more descriptors.

    Also, I know this post is old but the only thing that changed is for freeze alert. When you enter '(08) 24-hour auxiliary' there is no option for smkt3. Now it says 'freeze'.
    See this post for the sheet with new descriptors: http://www.2gigforum.com/threads/103...ce-Descriptors